The use of analysers for optimization of heaters is not uncommon, the control system used is a function of economic factors.
Damper control is done on forced draft heaters where the outlet damper on the induced flow fan is controlled together with the inlet air damper on the forced draft fan. This is done on both dampers simultaneously to avoid upsetting the combustion chamber pressure because of flow changes.
Losses of energy are measured by the oxygen content in the flue gases. Although temperature is the main item in enthalpy content of the flue gases, composition (=O2%) can be controlled and therefore heat losses minimized. It cannot be driven to zero because of the dangers posed by explosions, and the effects of incomplete combustion; the optimum value is determined by fuel type, heater characteristics and process heat loads. Because of the load relationship, the setpoint of the O2 controller must be programmed as a function of the load as developed from a series of tests. Air leaks and imbalanced burners reduce efficiency at all O2 levels, therefore, the heater needs to be monitored frequently on these items to assure that the programmed setpoint, stays, in fact, an optimum.
Alternatively, the concentration of CO could be used to manipulate the fuel-air ratio in the same way, especially on boilers. It is said that its optimum setpoint is independent of load, and is adjusted to minimize heat losses while avoiding smoke (soot) formation.