Recently, I had a project utilizing infiltration pavers. This is the approach I followed:
1. acquired infiltration testing.
2. used a CN of 100 in all paver areas.
3. created a "pond" for the paver base with % voids to create storage.
4. used the resulting rates from the infiltration testing (a 1/2 safety factor design rate) for exfiltration outlet.
5. created a weir outlet depicting overflow from excess runoff (what could not be exfilrated).