Focht3,
the reference is drawn from Bowles, your favourite textbook (
![[bigsmile] [bigsmile] [bigsmile]](/data/assets/smilies/bigsmile.gif)
).
The reference is the following:
Reese et al., 1976, "Behavoiur of drilled piles under axial loading", JGED, ASCE, vol 102, n.5,May, pp.493-510
The alpha reductive coefficient for Su along the pile shaft is reported to be 0.5 for dry holes or light slurries, and 0.3 for denser slurries, where removal of mudcake is uncertain.
This makes perfect sense and agrees with what you and BigHarvey said.
Looking up at Fang's treatise (Foundation Engineering Handbook), though, Kulawhy's article on drilled shafts, mention is made of more recent work (Reese and O'Neill, 1988, FHWA-HI-88-042 report, but not to bentonite slurries in connection with the alpha concept. Rather, he presents a graph with the alpha adhesion factor correlated to Su, with a mean non-linear trend given by:
alpha = 0.21 + 0.26(Pa/Su) <= 1.0, hence not related to the presence, the absence or the type of drilling fluid.
It may be that the early studies of Dr. Reese overrated the importance of slurries, or simply that conditions vary so much that, in some cases, a significant reductive factor is appropriate (according to Kulhawy this is the case with higher values of Su, > 1 tsf).
Just one more concept: the mudcake phenomenon and its plastering effect take place in permeable formations, with the presence of a gradient creating an outbound flow from the borehole to the surrounding soil. In impermeable layer this shouldn't occur. There might be though the presence of a thin film due to electrical forces beween soil and mud components, or other factors. Also, with a wet hole, there may be some clay softening effect which decreases Su and is translated into a lower alpha-value.
The model appears to grow of increasing complexity. Time is sure a main factor, mudcake and electrical phenomena need it to manifest properly.
To soilrocks, at this point I don't know wether a cased hole would give you a significantly higher lateral resistance with respect to a wet, uncased hole. In my area the introduction of bentonite slurries in lieu of steel casing increased contractors' profit by a substantial amount.
If the project is a large one it might be a good idea to experiment with a few load tests.
I find Focht3 and BigHarvey's observations very sensible.
By the way, do you guys calculate your drilled shafts based only on lateral resistance (minimum settlement) or on a combination of lateral and base resistance (higher settlements, hard to define precisely)? That is probably a tricky issue when load tests are not available.