Dear All,
I require your kind recommendations regarding the test results of pole voltage drop test carried out on one of our 6 pole synchronous motor as below.
In Feb-20, we have carried out the Pole Voltage drop test for rotor of motor and results found unsymmetrical to the tune of around 25% in one of the pole, which indicates shorting inside the rotor. The motor was sent for dry ice cleaning and then testing done again, no change in results found and then motor taken in line without any issues.
Subsequently Pole Voltage drop test done during the June-20,Jan-21 , on both occasions results found symmetrical, that is no short circuit. But recently during the Sep-21, we have again tested and again found pole voltage drop as unsymmetrical with around 12% variation in the same pole as found during Feb-20. Motor taken in line.
Motor is operating fine without any abnormal vibrations and all the operating parameters within limits.
I require your opinion on this and any further actions suggested.
I require your kind recommendations regarding the test results of pole voltage drop test carried out on one of our 6 pole synchronous motor as below.
In Feb-20, we have carried out the Pole Voltage drop test for rotor of motor and results found unsymmetrical to the tune of around 25% in one of the pole, which indicates shorting inside the rotor. The motor was sent for dry ice cleaning and then testing done again, no change in results found and then motor taken in line without any issues.
Subsequently Pole Voltage drop test done during the June-20,Jan-21 , on both occasions results found symmetrical, that is no short circuit. But recently during the Sep-21, we have again tested and again found pole voltage drop as unsymmetrical with around 12% variation in the same pole as found during Feb-20. Motor taken in line.
Motor is operating fine without any abnormal vibrations and all the operating parameters within limits.
I require your opinion on this and any further actions suggested.