Assuming that you are referring to pole slipping protection for synchronous generators, then the answer is that pole slipping (out of step) protection is usually provided by an impedance relay scheme that is set up generally as follows -
- A mho circle element
- Two impedance "blinders"
- Timer logic
The scheme is set so that the impedance locus will pass through the two parallel blinder characteristics for an unstable swing, with the mho circle set to act as a fault detector. During an unstable swing, the impedance locus will take a predetermined time to pass between the blinder charcteristics - this is processed by the timer logic which issues a trip command.
During an external fault, it is possible that the impedance locus will also fall within the operating zone of the scheme, but it will remain stationary and will not traverse bothe blinder characteristics. The logic will recognize this and block tripping. For a stable swing condition, the locus will not traverse the blinder zone fully and tripping will also be blocked.
I know that the above may be somewhat obsciure, but the topic is not an easy one - I have tried to give you a very general overview, which is difficult without diagrams.
This protection will be needed where there is a possibilty of generators falling out of step. The points made above by jbartos may be helpful in avoiding the situation; I would add the following -
- Improve fault clearing times to avoid machine instability
- Operate the machines with an adequate stability margin - avoid high or leading power factor operation
- Perform a comprehensive study of machine AVR and excitation systems to evaluate appropriate gain settings and to analyse whether power system stabilizers or other means of system stabilization are needed.