Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Polarization index 1

Status
Not open for further replies.

setiawanmarten

Electrical
Joined
Aug 17, 2011
Messages
13
Location
AU
Dear all,
I have this transformer 6000 kva , primer 11.000 v , sec 245 v, teh dga result was indicating high h2, i am planning to do polarization index, is it save to inject 500v dc to secunder for 10 minutes for pi test the secunder? (twice the nominal rating of the secundr)From the standard bellow 600 v i think it would be 1000 v?

Thank you

Marten
 
500VDC is acceptable. The recommended voltage for Insulation Resistance testing for windings <600V is 1kVDC per NETA Table 5, so 500V will not cause a problem.

Not sure what a PI test will tell you about hydrogen production. This is typically cause by partial discharge or hydrolysis.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top