The standard was revised in 2013. Under 12.2.2, it says "When the insulation resistance reading obtained after the voltage has been applied for 1 min (IR1) is higher than 5000 MΩ, based on the magnitude of applied direct voltage, the total measured current (IT) can be in the sub microampere range (see Figure 3). At this level of required test instrument sensitivity, small changes in the supply voltage, ambient humidity, test connections, and other non-related components can greatly affect the total current measured during the 1 min –10 min interval required for a P.I. Because of these phenomena, when the IR1 is higher than 5000 MΩ, the P.I. may or may not be an indication of the insulation condition and is therefore not recommended as an assessment tool."