Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Point Load Distribution

  • Thread starter Thread starter -
  • Start date Start date
Status
Not open for further replies.

Guest
Does anyone know of a good reference that addresses the issue of distributing a point load out through a wooden deck through to the supports. I have a point load that is applied to a 4" thick deck supported on cross members spaced at 3' on centre and I would like to know what percentage of load I can assign to each support
 
I assume that the deck is made up of beams or strips perpendicular to the supporting members; these would tend to act as simple beams rather than as a plate. Calculate the simple reactions (or possibly a three or four span analysis if the support beams form bays). The reactions should give you the plf load on the support beams. Of course, you have to include the deck design load as well.

Be careful of the locations of the ends of each strip; if you dont know the position of the point load with relation to the end of the strip, a simple beam calculation will be the safe way to go.

Tongue and groove decking could be a bit more problematic, but I would arbitrarily assume a beam width of 12 inches.

Also, make sure that the deck won't deflect excessively at the concentrated load.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top