During testing of our AVR, we reach about 58% output to the exciter and get a misfiring on one of our SCRs. The misfiring causes noise in our system, and because the noise is on the output of the exicter, the generator runs away (goes high) until our protection relay trips the exciter field breaker. Our AVR is using a PMG for input power. When we increase the output to 60% output to our unit, the noise goes away. We believe that the issue is due to EMI induced on the cabling going to the control circuit. Could the issue be our PMG? Could the switching noise of the SCRs be causing our PMG reference to be noisey and therefore impact our ouptut?
I am typically a small wire guy(I&C), so I am a bit out of my elelment on this issue.
Thanks,
Todd