Plumb deviation for a 50m steel chimney

Status
Not open for further replies.

rubsy

Civil/Environmental
Joined
Dec 16, 2004
Messages
4
Location
PH
What is the acceptable out of plumb deviation for a 50 meter steel chimney? At the moment the chimney that was erected is already at 27 meters and 5 inches out of plumb.
 
The last stucture like this that I was involved with had a max of 4" overall out of plumbness required. See Asme STS-1 code for Stacks.