Plugging and wrong DP output

EEENGRX

Electrical
Sep 11, 2021
94
I have a DP that is used to read Level in a scrubber. The scrubber has a demister somewhere around the top and from time to time It gets to plug between the valve and the transmitter which throws off the level readings and would then need to rely on a site glass to monitoring.What would be other options of getting around this issue or a way to permanently resolve these issues.All suggestions are very well appreciated IMG_4537.jpeg
 
Replies continue below

Recommended for you

Ask for remote seals on BOTH HP and LP sides of the dp cell - diaphragm seals - this should prevent any gunk / condensate from getting into the impulse lines.
 