PLS-CADD (Copper Conductor - Help Required)

Status
Not open for further replies.

Rejeckted

Electrical
Joined
Mar 7, 2021
Messages
37
Location
IN
Dear Friends,

We are supplying a 400 SQ.MM Bare Copper Conductor (Hard Drawn - HDCC) for Customer Substation Application for Busbars and Jumper Connection. Any idea how to get this data? I think PLS - CADD has similar interface.

Capture_em2aiy.jpg


Thanks
Chris
 
Are you using copper cable under tension? If this is only for flexible jumpers, most of the parameters may not be needed.

If this is for a common cable type, may have the parameters. Otherwise you (or the manufacturer) can send a chunk of the cable to a testing lab.
 
The offered 400sqmm Bare copper conductors are used for substation Busbar arrangement and equipment jumper connection. The Copper Conductor we offer is Soft.

59/2.92mm (Strand/Dia of strand)

Do I need to look into one of these right: ? So then 400 Sq.mm = 789.4 kcmil right?

Exact copper conductor with 59 strands is not available. I am asking for help because dont have license

Thanks
Chris
 
I tried that, I didnt understand how exactly to open that data?
 