CCCBuilder
Civil/Environmental
- Apr 5, 2023
- 6
Hey all. I'm wanting to learn how to properly size an LVL beam when the specifics do not simply fall under the manufacture's generic span chart giving two options for premade spans. I believe this is the PLF rating? It seems a little too straightforward using the tech sheet so I want to make sure I am calculating correctly.
The situation is as follows. A LVL beam to be installed to support ceiling joists that are *not* continuous, as in they tie into the LVL beam. The ceiling joists are for two rooms, each room for this example has a length of 14' so the "Span Carried" would be 28' but technically when I run the PSF I would halve this I assume?
The ceiling joists have 5/8" drywall - let's say 2 layers - and then attic space above with blow in insulation. The ceiling joists are 2x6, 16" OC. I was going to use 20PSF for this rating. 5PSF for attic dead load of insulation and 2x6 framing (stick framed with rafters, ridge board, etc and not webbed truss), 5PSF for two layers of drywall/mud, and 10PSF for what would be live load of someone crawling around in attic... I'd say that is more than 10PSF but online searches seem to treat person in attic as 10PSF?
The LVL beam needs to span 22'.
For the first part of this, I am taking 20PSF x 14' (half the 28') to get my PLF of 280. I then divide this by 2 and 3 to find my individual PLF capacity needed for 2 and 3 ply of LVL EDIT:If using a chart for single 1-3/4" only. In this case, the Georgia Pacific GP Lam LVL tech sheet has 1, 2, 3, and 4 plys already built in. I scroll down to the Allowable Uniform Floor Loads because it uses at least L/360 in this case since it is drywall that would be sagging here. When I comb through the chart, I locate 22' for the span and go across on the "Two 1-3/4" GP Lam LVL" (and three) to find the first LVL that can do 280 with 2 ply is a 16" LVL. and the first LVL to do 280 with 3 ply 14".
Can someone please tell me if this is the correct process, assuming I had a correct PSF to start with? I'm just looking for confirmation that I am not missing something here. It seems too easy simple, and I'd also like to know of any quick formula perhaps to convert the PLF rating of the LVL for less deflection like L480 when their chart maxes on 360. I was considering using the percentage change from their roof PLF (240) to their floor PLF (360) and multiplying that ratio to the numbers but I'm sure that's just shooting in the dark.
The situation is as follows. A LVL beam to be installed to support ceiling joists that are *not* continuous, as in they tie into the LVL beam. The ceiling joists are for two rooms, each room for this example has a length of 14' so the "Span Carried" would be 28' but technically when I run the PSF I would halve this I assume?
The ceiling joists have 5/8" drywall - let's say 2 layers - and then attic space above with blow in insulation. The ceiling joists are 2x6, 16" OC. I was going to use 20PSF for this rating. 5PSF for attic dead load of insulation and 2x6 framing (stick framed with rafters, ridge board, etc and not webbed truss), 5PSF for two layers of drywall/mud, and 10PSF for what would be live load of someone crawling around in attic... I'd say that is more than 10PSF but online searches seem to treat person in attic as 10PSF?
The LVL beam needs to span 22'.
For the first part of this, I am taking 20PSF x 14' (half the 28') to get my PLF of 280. I then divide this by 2 and 3 to find my individual PLF capacity needed for 2 and 3 ply of LVL EDIT:If using a chart for single 1-3/4" only. In this case, the Georgia Pacific GP Lam LVL tech sheet has 1, 2, 3, and 4 plys already built in. I scroll down to the Allowable Uniform Floor Loads because it uses at least L/360 in this case since it is drywall that would be sagging here. When I comb through the chart, I locate 22' for the span and go across on the "Two 1-3/4" GP Lam LVL" (and three) to find the first LVL that can do 280 with 2 ply is a 16" LVL. and the first LVL to do 280 with 3 ply 14".
Can someone please tell me if this is the correct process, assuming I had a correct PSF to start with? I'm just looking for confirmation that I am not missing something here. It seems too easy simple, and I'd also like to know of any quick formula perhaps to convert the PLF rating of the LVL for less deflection like L480 when their chart maxes on 360. I was considering using the percentage change from their roof PLF (240) to their floor PLF (360) and multiplying that ratio to the numbers but I'm sure that's just shooting in the dark.