I had an issue come up this week that I am curious about. I have always been told something on other jobs by my superiors at work but it is getting questioned on a job I am working on now by the architects and I can't find it explicitly in the code.
The issue is this: In an office environment, using a full plenum return, there always tend to be big open office areas mixed with enclosed offices and conference rooms that have walls extending to the drop-ceiling. I have always been told that there needs to be a dedicated return grilles in these walled offices and conference rooms since you cannot, by "code", base your design around the air being supplied to these enclosed offices but then transferring to the adjacent open office area to be returned.
I cannot find anything in the code against this other than stating that '*Corridors* shall not serve as supply, return, exhaust, relief or ventilation air ducts.' Well, these open office areas don't seem to fall under the definition of a corridor in the code.
Now, I am still currently designing my building this way with dedicated return grilles to the plenum but the architects are wanting me to do something different and code-wise I can't find a reason to back up the way I am doing it.
Has anyone else run into this? Other than the fact that the doors to the offices might not always be open and you'd have to provide door grilles to physically allow the air to transfer out to the open office area, what in the code would prevent me from transferring air from a walled office, to the adjacent open office area, and then to the the plenum?
The issue is this: In an office environment, using a full plenum return, there always tend to be big open office areas mixed with enclosed offices and conference rooms that have walls extending to the drop-ceiling. I have always been told that there needs to be a dedicated return grilles in these walled offices and conference rooms since you cannot, by "code", base your design around the air being supplied to these enclosed offices but then transferring to the adjacent open office area to be returned.
I cannot find anything in the code against this other than stating that '*Corridors* shall not serve as supply, return, exhaust, relief or ventilation air ducts.' Well, these open office areas don't seem to fall under the definition of a corridor in the code.
Now, I am still currently designing my building this way with dedicated return grilles to the plenum but the architects are wanting me to do something different and code-wise I can't find a reason to back up the way I am doing it.
Has anyone else run into this? Other than the fact that the doors to the offices might not always be open and you'd have to provide door grilles to physically allow the air to transfer out to the open office area, what in the code would prevent me from transferring air from a walled office, to the adjacent open office area, and then to the the plenum?