PLC input ripples

Status
Not open for further replies.

heshamzaki

Electrical
Feb 6, 2008
3
Dear All,

I would be grateful if someone helped me with this. I am planning to use ABB AC31 PLC. one of the inputs to the PLC will be the output of a single phase full wave rectifier uncontrolled bridge. when using smoothing reservoir capacitor, still the voltage will have some ripples.Are these ripples harmful to the plc? or i shouldn't care that much about them?

If I should totally gt rid of the ripples, how can i do that?

(by the way, the bridge output is inserted to analog input point of the plc)
 
Replies continue below

Recommended for you

Connect the plc input to the bridge output via a resistor of a couple of k[Ω] or so. Put a relatively small capacitor directly across the PLC input. The small cap will smooth out the ripple and the resistor will decouple it from the main supply. It won't be a perfect representation of the DC level + ripple, but your PLC isn't fast enough to care.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
I know on ab contrologix their is signal conditioning on inputs to look not look unless the signal changes over a predetermined time as configured on card. Siemens though has diagnostic ripple on its input cards, this might be a problem if using these type. This can be disabled Not sure on ABB plc. I would think they would have some scheme similar to above manufacturers, since they always seem to copy off of each other.
 