GalileoG
Structural
- Feb 17, 2007
- 467
I have steel girders, and joists spanning between girders. I am designing a structural platform to support a RTU, the platform will span from girder to girder above the roof.
The span of the platform beams at the two sides of the RTU is approximately 49ft (girder to girder distance); there are two secondary beams to pick up the other two edges of the RTU. There are no horizontal bracing or grating. The RTU is at mid-span.
The RTU weighs approximately 9 kips. I have taken into consideration wind acting on the RTU and the beams, and seismic load. I am taking the full length of the platform (49ft) as the unbraced length.
I have sized the platform beams to be a W14x74. The weak-axis deflection of this beam to wind load only is 1.5” (this is after multiplying the 2” deflection with a serviceability important factor for wind load of 0.75, as permitted in the Canadian code). The deflection comes to be L/400.
Even though I meet the very reasonable deflection requirement of L/400, a deflection of 1.5” due to wind load seems high. This also brings up another question of vibrations. Would vibrations be a concern and how would I go about checking it? (The RTU is a makeup air unit). Any other design considerations?
The span of the platform beams at the two sides of the RTU is approximately 49ft (girder to girder distance); there are two secondary beams to pick up the other two edges of the RTU. There are no horizontal bracing or grating. The RTU is at mid-span.
The RTU weighs approximately 9 kips. I have taken into consideration wind acting on the RTU and the beams, and seismic load. I am taking the full length of the platform (49ft) as the unbraced length.
I have sized the platform beams to be a W14x74. The weak-axis deflection of this beam to wind load only is 1.5” (this is after multiplying the 2” deflection with a serviceability important factor for wind load of 0.75, as permitted in the Canadian code). The deflection comes to be L/400.
Even though I meet the very reasonable deflection requirement of L/400, a deflection of 1.5” due to wind load seems high. This also brings up another question of vibrations. Would vibrations be a concern and how would I go about checking it? (The RTU is a makeup air unit). Any other design considerations?