The four columns are definitely shear/moment related requirements, what's geometrically required is top to bottom bolts spaced at X" apart. So the designer needs to figure out how many columns of top to bottom bolts he/she needs.
In the bygone days of ASD and LFD, the requirement was to design the splice for a percentage of the girder section with consideration for material properties. Thus even the smallest section of a large girder had an impressive splice arrangment.
That there are not splice plates on the end of this girder may indicate that plates are on the other piece that will recive the end of this girder. Steel shops will typically partially bolt the splice to one of the sections leaving just enough bolts holes open to pull in the next piece.
As an a example, I've seen smaller beams in buildings that the splice plate is only half or some fraction of the total web depth. And was likely deisgned to the loads. Under AASHTO guidelines you can not do that. You must have a full depth web plate.
Also, all bridge splices are designed as slip-critical and so friction resistance is the governing requirement. Bolts in bearing under LFD were checked as an ultimate condition.
It very well may be a transfer girder for a power plant or even something else, but it just looks like a typical bridge girder to me.
For structural steel to be at it's best when competing with a local prestress, precast fabricator, steel leaves all behind at the 250 to 300 range and upward. Steel is much ligher than concrete at those spans - though nowadays spliced prestressed girders are pushing longer spans, up to 300', they remain heavier requiring heavier foudations.
Either way I just like big girders!
Regards,
Qshake
![[pipe] [pipe] [pipe]](/data/assets/smilies/pipe.gif)
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.