MatthewL
Chemical
- Jul 22, 2011
- 77
I am looking for some confirmation of a few calculations I am working on. Right now, we use a plate and frame heat exchanger with water on both sides to cool process water using either cooling tower water or chilled water. I took some readings on a recent run using tower water, and here were the results:
SIDE TEMP IN TEMP OUT FLOW(GPM)
HOT 109 F 100 F 168 (metered)
COLD 79 F 89 F 151 (calculated)
I trended the results over the last year, and our normal hot in/hot out delta is +/- 1 degree of a 10 degree delta, meaning the plates are likely not going to be any more fouled than they are now. Checking the duty, I come up with ~900,000 BTU/hr (m*cp*delta T). The plate and frame has 65 plates at 1.5 sqft/plate, so back calculating for U gives (by rearranging Q = U * A * delta T):
(900,000 BTU/hr) / (20 F * 65 * 1.5 sqft) = 462 BTU/F sqft hr
We are looking at a new product that will require process water at 65 F and our chilled water is at ~55 F. Since the current approach (hot in/cold out) is 20 F, obviously (assuming constant U) we don't have enough area to force the approach. More likely would be a 75 F hot side out, assuming that the U is constant. Since the approach is half as much, the number of frames needed should be 130, correct? Also, we may be able to drive our chilled water down another 5 degrees, meaning we need a 15 degree apporoach. This would give 65 plates * 20 F / 15 F = 87 plates, assuming again that the U is constant even though we have reduced the flow rate. As a side note, this exchanger was originally designed with 95 plates, but the original plate design is no longer available, and we are now using a higher efficiency plate. I know the plate is higher efficiency because we are still meeting design spec with 65 plates. Here's where things get squirrely. I contact our local heat exchanger rep and give him the same numbers and ask him to check with Alfa Laval what we should do. He comes back with the current setup should be able to meet our needs without adding plates! I don't get it. Is my math off? I know I made some assumptions, but if anything I would have thought I would need MORE plates than I calculated. My current inclination is to run the chiller at 50 F and add 25 plates, for a total of 90 plates. Any thoughts?
Thanks,
Matt
Quality, quantity, cost. Pick two.
SIDE TEMP IN TEMP OUT FLOW(GPM)
HOT 109 F 100 F 168 (metered)
COLD 79 F 89 F 151 (calculated)
I trended the results over the last year, and our normal hot in/hot out delta is +/- 1 degree of a 10 degree delta, meaning the plates are likely not going to be any more fouled than they are now. Checking the duty, I come up with ~900,000 BTU/hr (m*cp*delta T). The plate and frame has 65 plates at 1.5 sqft/plate, so back calculating for U gives (by rearranging Q = U * A * delta T):
(900,000 BTU/hr) / (20 F * 65 * 1.5 sqft) = 462 BTU/F sqft hr
We are looking at a new product that will require process water at 65 F and our chilled water is at ~55 F. Since the current approach (hot in/cold out) is 20 F, obviously (assuming constant U) we don't have enough area to force the approach. More likely would be a 75 F hot side out, assuming that the U is constant. Since the approach is half as much, the number of frames needed should be 130, correct? Also, we may be able to drive our chilled water down another 5 degrees, meaning we need a 15 degree apporoach. This would give 65 plates * 20 F / 15 F = 87 plates, assuming again that the U is constant even though we have reduced the flow rate. As a side note, this exchanger was originally designed with 95 plates, but the original plate design is no longer available, and we are now using a higher efficiency plate. I know the plate is higher efficiency because we are still meeting design spec with 65 plates. Here's where things get squirrely. I contact our local heat exchanger rep and give him the same numbers and ask him to check with Alfa Laval what we should do. He comes back with the current setup should be able to meet our needs without adding plates! I don't get it. Is my math off? I know I made some assumptions, but if anything I would have thought I would need MORE plates than I calculated. My current inclination is to run the chiller at 50 F and add 25 plates, for a total of 90 plates. Any thoughts?
Thanks,
Matt
Quality, quantity, cost. Pick two.