BAretired said:
Perhaps we are defining the cutoff point in a different way. I say the cutoff point is the location where the full length reinforcement is just able to resist the moment by itself.
No, we've been thinking of the same theoretical cutoff point BA.
BAretired said:
thus there is no demand on the additional reinforcement at the cutoff point
BAretired said:
If concentrated loads were added each end of the beam between points A and B, keeping the uniform load the same throughout, Mb would increase, creating greater demand on the full length reinforcement but the additional reinforcement would be unaffected by it because Mc - Mb would not change. There would still be no demand on the additional reinforcement at the theoretical cutoff point.
Based on the above statements, I believe that our difference of opinion stems from our telling two different stories regarding the flexural tension demand in the rebar at the cutoff locations. See my sketch below and let me know if it fails to accurately reflect your thinking.
With steel reinforcing of steel beams, the MQ/I story is saying that:
1) Immediately to the left of the theoretical cutoff point, all stresses are distributed in MC/I fashion throughout the unreinforced section and;
2) Immediately to the right of the theoretical cutoff point, all stresses are distributed in MC/I fashion throughout the reinforced section.
Making that pseudo-instantaneous jump is what creates the MQ/I and tension lag demands immediately beyond the cutoff point. My story of cutoff rebar flexural tension demand is consistent with the MQ/I philosophy. Your story is not. And that's not to say that my story is more correct than yours or, indeed, that my story is correct
at all. Mine simply parallels MQ/I methodology. I also feel that my story is more compatible with strain compatibility (pun intended). But then, we assume strain compatibility in concrete in many instances where it clearly doesn't exist.
I've reviewed a few of the concrete textbooks that I have on hand with regard to this issue. All simply state that, for a number of reasons, bars should be extended beyond the theoretical cutoff point. And I don't dispute that will produce safe designs regardless of which of our stories more closely reflects the truth.
I was hoping that I could find something in print that would make one of our flexural tension demand stories the clear winner but, so far, I've come up empty handed. I've included MacGregor's version below for reference. It deals with overall, mobilizeable code capacity but doesn't say much regarding the expected stress in individual bars.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.