I just received plan check corrections for a two story light wood framed residential remodel that I did the engineering for located in Southern California.
Scope included removal of an existing shear wall at one location in the house, and elements of the vertical resisting system changed as well.
We have the as built Structural plans that were approved in 2001 and they clearly labeled all of the existing shear walls and their capacities. This falls under the 97 UBC
I addressed the removal of the existing shear wall by using the plans to determine the rated capacity of that SW and multiplying that by the SW's length to get the total lateral force along that line that needs to be resisted by 2 new shear walls. Unfortunately this creates a vertical type 4 irregularity. Therefore I designed the new floor beams for the uplift and compression forces to include the Omega factor.
One of the plan check corrections states that the Seismic design shall be based on the equivalent lateral force procedure using a redundancy factor rho = 1.3.
3 questions:
1) What are your thoughts on the design approach I used to account for the removal of the existing shear wall?
2) I know that in the 97 UBC they utilized a redundency factor but in order to determine that now I would have to perform a complete lateral analysis and vertical distribution of seismic forces which is what I am trying avoid by using the existing structural plans.
3) There is an exception in ASCE 7-10 (12.4.3.1) for the use of the Omega factor. For anyone who is familiar with this exception is this saying that I don't have to design the beams supporting the shear walls for the uplift/compression forces with omega = 2.5 as long as I design the beam for the maximum forces that can be developed in that shear wall sitting on top of the beam?
Thanks for your help.
Scope included removal of an existing shear wall at one location in the house, and elements of the vertical resisting system changed as well.
We have the as built Structural plans that were approved in 2001 and they clearly labeled all of the existing shear walls and their capacities. This falls under the 97 UBC
I addressed the removal of the existing shear wall by using the plans to determine the rated capacity of that SW and multiplying that by the SW's length to get the total lateral force along that line that needs to be resisted by 2 new shear walls. Unfortunately this creates a vertical type 4 irregularity. Therefore I designed the new floor beams for the uplift and compression forces to include the Omega factor.
One of the plan check corrections states that the Seismic design shall be based on the equivalent lateral force procedure using a redundancy factor rho = 1.3.
3 questions:
1) What are your thoughts on the design approach I used to account for the removal of the existing shear wall?
2) I know that in the 97 UBC they utilized a redundency factor but in order to determine that now I would have to perform a complete lateral analysis and vertical distribution of seismic forces which is what I am trying avoid by using the existing structural plans.
3) There is an exception in ASCE 7-10 (12.4.3.1) for the use of the Omega factor. For anyone who is familiar with this exception is this saying that I don't have to design the beams supporting the shear walls for the uplift/compression forces with omega = 2.5 as long as I design the beam for the maximum forces that can be developed in that shear wall sitting on top of the beam?
Thanks for your help.