JohnWeal
- Dec 16, 2012
- 124
Assume pump discharge is at zero metres elevation.
horizontal discharge for 8m length then turns vertical for 18m to an open-ended free discharge.
(Diameter from pump is 700mm then imediately increased to an 800mm pipeline)
There is no non return valve in th line or isolation valves. (previous pump installation for this sewage duty found it beneficial to have the flow come back and back spin the cetrifugal pump which help clear rags etc)
Upstream of the pump assume 1m above pump centre-line which gives a 17m static head. (The upstream head will not vary due to backflow as the volume is large within the sewer)
I need to check that the pipe forces produced due to the backflow (pump trip perhaps being the worst case rather than controlled turn-down) when acting upon the reducer immediately fitted to the pump discharge flange. (and hence the load on the pipe support to prevent loads being transmitted to the pump)
Any advice on this type of calculation?
I was thinking Bernoulli's equation but think as the riser starts to empty and the flow returns to the channel upstream of the pump, the head is reducing but also the velocity is higher as momentum of the fluid gathers.
John
John