I have two existing buildings with dedicated fire services. For joints I have called out either flanged joints, mechanical joints or a combination of the two for restraint. I have also given the contractor the option to use thrust blocks with the appropriate sizes called out per plan.
Typically, I understand mechanical joints such as the EBBA Iron Megalug to allow you the transfer of thrust forces from the water to the megalug to the pipe where it gets transfer to the soil via friction between the pipe and the soil with no thurst block required. This would assume that you have enough length of pipe to develop the capacity due to friction to take on that transferred thrust force. Otherwise the force would get transferred to any thrust blocks. Since many of the pipe runs are relatively short in length, I have called out the use of mechanical joints in addition to the thrust blocks.
Am I been over conservative? The contractor would like to know as to why he can't just use push on joints with thrust blocks. By the way, fire lines are tested and are operated at higher pressures than domestic lines, therefore the extra factor of safety, in my opinion, can only be a good practice. Am I missing something? Your thoughts! Thank you.
Typically, I understand mechanical joints such as the EBBA Iron Megalug to allow you the transfer of thrust forces from the water to the megalug to the pipe where it gets transfer to the soil via friction between the pipe and the soil with no thurst block required. This would assume that you have enough length of pipe to develop the capacity due to friction to take on that transferred thrust force. Otherwise the force would get transferred to any thrust blocks. Since many of the pipe runs are relatively short in length, I have called out the use of mechanical joints in addition to the thrust blocks.
Am I been over conservative? The contractor would like to know as to why he can't just use push on joints with thrust blocks. By the way, fire lines are tested and are operated at higher pressures than domestic lines, therefore the extra factor of safety, in my opinion, can only be a good practice. Am I missing something? Your thoughts! Thank you.