Obviously not as many as I have, but that is why I qualified my comment to apply specifically to those pipelines.
However I fail to see why anyone would purposely put a material potentially containing high void ratios under a load bearing structure of any kind. How many petroleum pipelines does the USACOE construct. They actually do short ones, but what's the point. Better to address the concerns I listed.
USACOE (from the Unified Specifications) recommends the following grades Type I and II for utility bedding material. This would not preclude the use of gravel in specific locations for particular engineering intent, however the OP question is general, not for any specific concern, so I believe this is relevant and applicable to the question on general utility bedding requirements.
2.3 UTILITY BEDDING MATERIAL
Except as specified otherwise in the individual piping section, provide
bedding for buried piping in accordance with AWWA C600, Type 4, except as
specified herein. Backfill to top of pipe shall be compacted to 95
percent of ASTM D698 maximum density. Plastic piping shall have bedding
to spring line of pipe. Provide ASTM D2321 materials as follows:
a. Class I: Angular, 6 to 40 mm 0.25 to 1.5 inches, graded stone,
including a number of fill materials that have regional significance
such as coral, slag, cinders, crushed stone, and crushed shells.
b. Class II: Coarse sands and gravels with maximum particle size of 40 mm
1.5 inches, including various graded sands and gravels containing
small percentages of fines, generally granular and noncohesive, either
wet or dry. Soil Types GW, GP, SW, and SP are included in this class
as specified in ASTM D2487.
TABLE 1
[Type I
[Gradation E
11
ASTM C33/C33M]]
[Type II
[Gradation 57
ASTM C33/C33M]]
[ASTM D422 Sieve Size]
[Percent Passing] Type I Type II
[37.5 mm] [1.5 inches] [--] [100]
[25.0 mm] [1 inch] [--] [90 - 100]
[9.5 mm] [3/8 inch] [100] [25 - 60]
[4.75 mm] [No. 4] [95 - 100] [5 - 40]
[2.36 mm] [No. 8] [--] [0 - 20]
[1.18 mm] [No. 16] [45 - 80] [--]
[300 micrometers] [No. 50] [10 - 30] [--]
[150 micrometers] [No. 100] [0 - 10] [--]