Pilot operated safety valves used on an economizer

Status
Not open for further replies.

MSPVIN

Industrial
Joined
Oct 15, 2018
Messages
11
Location
US
when sizing and selecting a safety valve for the economizer what sizing methodology do you use?

 
There is a detailed discussion in this Pentair document:


The fundamental problem to be addressed here is a water filled economizer that becomes blocked-in while still exposed to hot gasses. Tube rupture can occur.

Basically, the safety relief valve must be sized for a specific massflow in both steam and water.

The rated capacity of these safety relief valves is determined by the economizer manufacturer based upon the maximum heat absorption rate.

Hope that this helps .....

MJCronin
Sr. Process Engineer
 
very well explained, thank you
 