Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pile Splice Location

Status
Not open for further replies.

GoDucks

Structural
Nov 1, 2005
27
The Contractor on a steel pile trestle bent bridge has proposed placing a welded pile splice within the concrete pile cap.

The pile (PP36x1.0) is embedded 36" into the cap and they wish to splice it 4" into the cap (prefabbed top 32" piece)

Would you have a concern in splicing that close to the top? The details of the bent assume that some moment will be developed at the connection and be transferred into the pile.
 
Replies continue below

Recommended for you

If the pile had needed to be spliced in order to drive it to its required depth or capacity, and if the splice just happened to wind up at 4" above the cap subgrade, would you still be asking this question? Probably not. It seems to me that, if the pile will be spliced properly, there should not be a problem.

 
Additionally, if the pipe pile is going to be filled with concrete there would be even less issues.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor