Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

pile load test

Status
Not open for further replies.

geo321

Civil/Environmental
Joined
May 17, 2015
Messages
85
Location
BE
Good day

we are currently preparing a pile load test.the head of the pile is a little bit broken as per the attachement.
1- is it ok or it must be repaired ?
2- how much the pile should be extended above the exacavated soil level ?
 
 http://files.engineering.com/getfile.aspx?folder=fd16fbdf-a630-4dd3-bf1d-84973b45c87f&file=20150520_100649.jpg
I suspect the head area is weaker concrete or grout than below, possibly high W/C ratio. It would seem that all the weak area should be removed and a strong zone of new grout or concrete should replace it. Bond the new to the old with a Portland cement paste applied to dry undisturbed material. Cure the new patch as necessary to gain strength before the test is run.

Projecting part of pile can be more than shown, if needed.
 
Cut the top of the pile to good concrete. Load test. Then expose rebar and splice to bring up to required level or increase the thickness of the pile cap to accommodate cut.
 
I agree with oldestguy that pile head is weaker, this should chip to the fresh concrete and rebuilt using the high strength grout.
An 500mm excavation around the pile may be required to get a space to place the dial gauges.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top