Hi all,
Here is the context of my question. I am working as a civil engineer doing drainage design, flood assessment etc for a new school development. The building is a 4 storey structure. We are also doing some earthworks design. As part of the earthworks design I had to review to geotech report to get an idea on what soil types im dealing with. This is when I came across the foundation section of the report.
The borelogs show SPT testing and shear vane testing every 1.5 - 2m. SPT then 1m deeper SVT then SPT and so on.
There is a layer of made ground to a depth of roughly 2m, broken concrete, glass etc, so definitely not suitable to support foundations. From 2m depth the soils are silty clay and clay. Uncorrected N values are as follows:
10 - 15N from 2m to 10m Cu of 40 - 60kPa from 2 - 6m
20 - 28N from 10 - 15m 80 - 90kPa from 6 - 10m
100 - 110kPa from 10 - 15m
The geotech have gone for bored piles since we are near some existing buildings and vibrations from pile driving would be an issue. In particular CFA piles over bored-cast in place as with bored pile you would need temp/permanent casing thorough made ground. I agree with all of this so far.
When assessing pile capacity they have used Qb base capacity = Nc * Ap * Su (with Nc = 9)
and,
Qs shaft capacity = As(area of shaft) x fs (shaft Friction in kPa)...........fs = α * Su
They have used the Stroud correlation of 4.5N = Su.
Surely using Su or Cu from the in - situ shear vane test would be the most appropriate to use?
Here is the context of my question. I am working as a civil engineer doing drainage design, flood assessment etc for a new school development. The building is a 4 storey structure. We are also doing some earthworks design. As part of the earthworks design I had to review to geotech report to get an idea on what soil types im dealing with. This is when I came across the foundation section of the report.
The borelogs show SPT testing and shear vane testing every 1.5 - 2m. SPT then 1m deeper SVT then SPT and so on.
There is a layer of made ground to a depth of roughly 2m, broken concrete, glass etc, so definitely not suitable to support foundations. From 2m depth the soils are silty clay and clay. Uncorrected N values are as follows:
10 - 15N from 2m to 10m Cu of 40 - 60kPa from 2 - 6m
20 - 28N from 10 - 15m 80 - 90kPa from 6 - 10m
100 - 110kPa from 10 - 15m
The geotech have gone for bored piles since we are near some existing buildings and vibrations from pile driving would be an issue. In particular CFA piles over bored-cast in place as with bored pile you would need temp/permanent casing thorough made ground. I agree with all of this so far.
When assessing pile capacity they have used Qb base capacity = Nc * Ap * Su (with Nc = 9)
and,
Qs shaft capacity = As(area of shaft) x fs (shaft Friction in kPa)...........fs = α * Su
They have used the Stroud correlation of 4.5N = Su.
Surely using Su or Cu from the in - situ shear vane test would be the most appropriate to use?