Pile cap action in auger cast piles 1

Status
Not open for further replies.

BAGW

Structural
Jul 15, 2015
392
Hi,

I have a situation where a column is supported on a pile cap bridging between 2 piles. Attached is the image below. Column reaction is in the range of 300kips.

Pile cap is 4'-0" deep and auger-cast piles are 18" in dia. Auger cast piles are deep enough to support the 150 kips of reaction through skin friction.

When I run the analysis for the pile cap design, I get more like a simple supported behavior for a pile cap rather than a fixed behavior (which I thought would be). Is the simply supported behavior because of the cap being so much more rigid than the piles? Has anyone run into such a situation?

Thanks
Document1_bge4wh.jpg
 
Replies continue below

Recommended for you

Yes. It is similar to a frame with the beam is much stiff than the column (pile). If modeled correctly, the pile should have a negligible amount of the moment.
 
yup. The column has negligible moment.

Ok so its the stiffness btw the two that's causing the simple behavior rather than fixed. Thanks
 
I would recommend doing a Strut and tie analysis. It's likely that your piles are 4.5' apart at 18".
 
The bending moment at the top of pile is partly dependent on the vertical doweling between the pile and cap.
If you have detailed, say, (8) #6 bars as vertical dowels, the top of pile will attract a bit of bending moment demand with just a small amount of rotation.
So what is your doweling?
And what is the clear span?
And when you say "run the analysis", that depends on what you told your software / spreadsheet to do. If there is fixity at the connection, of course you will attract moment. If you include a pin, then of course you will attract zero moment.

BTW, is there any relevance to ACIP vs CIDH or any other pile type?
 
I am detailing the piles as fixed. There are dowels at the top of pile and also there are horizontal rebar at the top of the pile cap. Even if I detail it as fixed, I am getting a small negative bending at the pile as the piles are very flexible compared to the pile cap.

I am modeling them in Risa and I have modeled the caps and the pile as continuous frames. Also I have modeled horizontal soil springs.

I agree with r13, because the cap is very rigid compared to piles, this has more of a simply supported behavior
 


The pile cap is 4'-0" deep and the piles are 18" in dia. and apparently the piles 4.5 -5 ft apart. That is, the shear span ( distance from face of the column to pile center ) to pile cap depth ratio is less than 1.0 and truss action will be dominant rather than bending action. I agree with slickdeals and a pink star to him for his comment (I would recommend doing a Strut and tie analysis. It's likely that your piles are 4.5' apart at 18".)

If you design the pile cap as bending element , the tension force for T=PL/(4d) ,( d= depth of pile cap ) and you would not need shear reinforcement. However, when overloaded, may exhibit brittle failure due to a small amount of longitudinal reinforcement and may not have any transverse shear reinforcement.

I will suggest also , STM and provide transverse shear reinforcement.
 
If you design the pile cap as bending element , the tension force for T=PL/(4d) ,( d= depth of pile cap ) and you would not need shear reinforcement.

ACI no longer has deep beam provision?
 




I have ACI 318 -14 and regarding the pile caps 13.4.2 , the code specifies the design with sectional method (designed for flexure and shear at assumed critical sections ) and allows the use of STM (13.2.6.3 Foundation design in accordance with strut-and tie modeling, Chapter 23, shall be permitted ).

Section 9.9—Deep beams ( 9.9.3.1 ) specifies min. distributed reinforcement along the side faces of deep beams.
 
Thanks. At one point of time, I thought they want to switch to STM entirely.
 




This is my respond to similar thread=

My interpretation of ACI 318 for the pile cap design is, satisfy the shear strength requirement for one way or two way shear ( if two way is applicable) and choose the reinforcement for flexural. That is, design for for flexure and shear at assumed critical sections .

If a pile cap is designed and satisfy two conditions, ACI will be a good shield . But , IMO,in order to sleep with comfort, a reinforcement cage should be provided for pile caps having more than 3 piles and for two piles case, the cap should be designed as beam element and minimum transversal shear reinforcement should be provided.
 