BigMotorGuy
Electrical
- Jul 27, 2009
- 56
I work at an induction motor manufacturer and we routinely do PI tests on newly constructed 3 phase stators. All the info I have read on PI ratios says anything below 2 is suspect. However, we routinely test smaller (e.g. 10Hp, 380v 2 pole) random wound stators measure very near 1. It appears when running the PI test, that the resistance reaches its maximum (i.e. current becomes near constant/minimum) well before 1 minutes (20 seconds in many cases), so the 1 minute reading is very near the 10 minute reading. We have never experienced a ratio below 1, but a ratio of 1 is not uncommon. The 1 minute resistance values are usually 50GOhms (or greater since meter maxes out at 50GOhms)so we know the insulation system if good. However, the larger form wound units (>300Hp, >690v) having PI ratios over 4 is quite common and considered acceptable by all accounts.
All the recommendations say anything below 2 is suspect, so is this such an uncommon issue for PI results being 1 on new, small random wound stators?
Thanks to All.....
All the recommendations say anything below 2 is suspect, so is this such an uncommon issue for PI results being 1 on new, small random wound stators?
Thanks to All.....