Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

PI Test and Dielectric Absorbtion test on motors

Status
Not open for further replies.

HamidEle

Electrical
Feb 20, 2007
309
planning to test on motors for our facility. wonder what would be a cost-effective plant for testing motors.
Other than IR test, should we consider PI test and Dielectric absorbtion test on larger motors particularly? Say PI on MV motors, and Dielectric AB on LV motors larger than 200hp?
 
Replies continue below

Recommended for you

My bad. I misunderstood the terms. There are definitions in NETA standard. Dielectric absorption is used for 200hp and less. PI is used for larger than 200hp.
but not sure if PI test is overkilled for LV Motors.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor