Dear all,
sorry for the long post.
During the design of two big photovoltaic power plants, the first one connected to the national HV grid and the second one isolated, manufacturers of inverters were not able to give some answers about the behaviour of their devices in steady state conditions and during transients.
Let me remark that I’m not interested in knowing what happens exactly inside an inverter. I have to make some power system studies (load flow, short circuit, and dynamics), so I will treat it as a black box.
Indication of papers or books will be appreciated.
=================================
Power plant in parallel with the HV grid
Steady state operation
AC side
1. Are voltage and frequency imposed by HV grid?
2. Is the inverter synchronised with the grid voltage?
3. What happens if the grid is disconnected?
4. What are the criteria for the production and regulation of P and Q?
5. Is a capability curve (like that of a synchronous generator) available?
DC side
6. What are the quantities regulated by the inverter on this side?
7. Operating in MPPT, does the inverter regulate the V to obtain the desired I?
8. From the point of view of the PV field, can the inverter be considered as a (variable) resistor?
9. AC and DC regulations can not be independent, since the inverter controls a power flux from DC to AC side. How do these regulations affect each other? Does the MPPT prevail on the P and Q production on the AC side?
Transients
1. Short circuit on the AC side. What are the inverter contributions in terms of symmetrical and direct components as defined in IEC 60909-0?
2. Short circuit on the DC side. What is the inverter contribution as defined in IEC 61660?
3. In case of opening of a remote circuit breaker whose state is unknown, the power system is isolated without any direct information about the grid connection. What happens?
4. What happens in case of a sudden connection or disconnection of a load? What is the behaviour of the inverter and how fast is its reaction to the transient?
5. What happens in case of loss of a string? What is the behaviour of the inverter and how fast is its reaction to the transient?
6. Similar to the AVR models described in the IEEE Std 421.5, Is there any kind of mathematical model of the inverter regulator as Laplace transfer functions?
=================================
Isolated Power Plant
Steady state operation
AC side
1. Are voltage and frequency imposed one inverter? Are the other possible inverter synchronised to this one?
2. What are the criteria for the production and regulation of V and f?
3. Can I consider a proportional (droop) or proportional + integral (isochronous) regulation of P and Q?
4. Is a capability curve (like that of a synchronous generator) available?
DC side
5. What are the quantities regulated by the inverter on this side?
6. Can the inverter regulate in MPPT or does the AC side regulation prevail?
7. From the point of view of the PV field, can the inverter be considered as a (variable) resistor?
Transients
8. Short circuit on the AC side. What are the inverter contributions in terms of symmetrical and direct components as defined in IEC 60909-0?
9. Short circuit on the DC side. What is the inverter contribution as defined in IEC 61660?
10. What happens in case of a sudden connection or disconnection of a load? What is the behaviour of the inverter and how fast is its reaction to the transient? Does the frequency vary? (In case of rotating generators, the frequency decreases because generators slow down, but I suppose that in this case frequency should be fixed by an oscillating circuit internal to the inverter)
11. What happens in case of loss of a string? What is the behaviour of the inverter and how fast is its reaction to the transient?
12. Similar to the AVR models described in the IEEE Std 421.5, Is there any kind of mathematical model of the inverter regulator as Laplace transfer functions?
=================================
Thank you very much
Best Regards
Alex68
sorry for the long post.
During the design of two big photovoltaic power plants, the first one connected to the national HV grid and the second one isolated, manufacturers of inverters were not able to give some answers about the behaviour of their devices in steady state conditions and during transients.
Let me remark that I’m not interested in knowing what happens exactly inside an inverter. I have to make some power system studies (load flow, short circuit, and dynamics), so I will treat it as a black box.
Indication of papers or books will be appreciated.
=================================
Power plant in parallel with the HV grid
Steady state operation
AC side
1. Are voltage and frequency imposed by HV grid?
2. Is the inverter synchronised with the grid voltage?
3. What happens if the grid is disconnected?
4. What are the criteria for the production and regulation of P and Q?
5. Is a capability curve (like that of a synchronous generator) available?
DC side
6. What are the quantities regulated by the inverter on this side?
7. Operating in MPPT, does the inverter regulate the V to obtain the desired I?
8. From the point of view of the PV field, can the inverter be considered as a (variable) resistor?
9. AC and DC regulations can not be independent, since the inverter controls a power flux from DC to AC side. How do these regulations affect each other? Does the MPPT prevail on the P and Q production on the AC side?
Transients
1. Short circuit on the AC side. What are the inverter contributions in terms of symmetrical and direct components as defined in IEC 60909-0?
2. Short circuit on the DC side. What is the inverter contribution as defined in IEC 61660?
3. In case of opening of a remote circuit breaker whose state is unknown, the power system is isolated without any direct information about the grid connection. What happens?
4. What happens in case of a sudden connection or disconnection of a load? What is the behaviour of the inverter and how fast is its reaction to the transient?
5. What happens in case of loss of a string? What is the behaviour of the inverter and how fast is its reaction to the transient?
6. Similar to the AVR models described in the IEEE Std 421.5, Is there any kind of mathematical model of the inverter regulator as Laplace transfer functions?
=================================
Isolated Power Plant
Steady state operation
AC side
1. Are voltage and frequency imposed one inverter? Are the other possible inverter synchronised to this one?
2. What are the criteria for the production and regulation of V and f?
3. Can I consider a proportional (droop) or proportional + integral (isochronous) regulation of P and Q?
4. Is a capability curve (like that of a synchronous generator) available?
DC side
5. What are the quantities regulated by the inverter on this side?
6. Can the inverter regulate in MPPT or does the AC side regulation prevail?
7. From the point of view of the PV field, can the inverter be considered as a (variable) resistor?
Transients
8. Short circuit on the AC side. What are the inverter contributions in terms of symmetrical and direct components as defined in IEC 60909-0?
9. Short circuit on the DC side. What is the inverter contribution as defined in IEC 61660?
10. What happens in case of a sudden connection or disconnection of a load? What is the behaviour of the inverter and how fast is its reaction to the transient? Does the frequency vary? (In case of rotating generators, the frequency decreases because generators slow down, but I suppose that in this case frequency should be fixed by an oscillating circuit internal to the inverter)
11. What happens in case of loss of a string? What is the behaviour of the inverter and how fast is its reaction to the transient?
12. Similar to the AVR models described in the IEEE Std 421.5, Is there any kind of mathematical model of the inverter regulator as Laplace transfer functions?
=================================
Thank you very much
Best Regards