phi factor for shear friction in seismic

Status
Not open for further replies.

Prestressed Guy

Structural
May 11, 2007
390
The typical ø I see in shear friction examples is 0.75 per table 21.2.1 for shear.
In SDC D Intermediate Precast Shear walls does it need to be 0.60 per 21.2.4?
 
Replies continue below

Recommended for you


You are expected to modify the value of ϕ for shear in accordance with 21.2.4.1 , 21.2.4.2 , and 21.2.4.3.

 