We have a project at substation where the transformer have delta secondary windings. The windings supply metal clad switchgear through U/G cable (PILC would be my guess by observation). The metal clad supplies a 13.8 kV distribution system. There is no sign of a grounding reactor at the substation but there may be one in the metal clad (I have been unable to find a single line for the metal clad but one is on the way).
The transformers will be upgraded in two years and may be changed from delta to wye (requiring all of the buswork and protections to be re-done, I would guess).
We want to meter on the LV side of the power transformers using standard three element metering. This will measure properly and allow use of easily available off-the-shelf VTs.
But...the VTs would be connected phase to ground. Every thing else is connected phase-phase. There is a ground detection system, indicating voltmeter and annunciation. No trace of automatic protection that I can find as yet.
The maximum voltage on the system is 13.8kV + 6% for ULTC = 14.63kV. The VTS are rated 15.96kV for 30 seconds, so they will stand up to full phase-phase voltage ... for a little while.
Would anyone have any experience hooking VTs phase-to-ground on a delta system. The VTs will supply revenue metering only about 6 VA max.
Is it just too risky since grounds may hang on longer than 30s?
Any advice?
We have a project at substation where the transformer have delta secondary windings. The windings supply metal clad switchgear through U/G cable (PILC would be my guess by observation). The metal clad supplies a 13.8 kV distribution system. There is no sign of a grounding reactor at the substation but there may be one in the metal clad (I have been unable to find a single line for the metal clad but one is on the way).
The transformers will be upgraded in two years and may be changed from delta to wye (requiring all of the buswork and protections to be re-done, I would guess).
We want to meter on the LV side of the power transformers using standard three element metering. This will measure properly and allow use of easily available off-the-shelf VTs.
But...the VTs would be connected phase to ground. Every thing else is connected phase-phase. There is a ground detection system, indicating voltmeter and annunciation. No trace of automatic protection that I can find as yet.
The maximum voltage on the system is 13.8kV + 6% for ULTC = 14.63kV. The VTS are rated 15.96kV for 30 seconds, so they will stand up to full phase-phase voltage ... for a little while.
Would anyone have any experience hooking VTs phase-to-ground on a delta system. The VTs will supply revenue metering only about 6 VA max.
Is it just too risky since grounds may hang on longer than 30s?
Any advice?