Hello,
We have recently installed a 15MVA , 66/11kv, Dyn11 transformer of which cooling is ONAN. Unfortunately we lost its manual from our station. When it was fully loaded we found that the Winding Temperature and Oil Temperature is compared other generator transformers in the same station. Which are ONAF and of different make. When we checked the name plate details we found the following details:
Maximum permissible Ambient Temperature: 50 degree Centigrade
Maximum Temperature rise above Ambient Temeprature for Oil/Winding: 50/55 degree Centigrade.
When we checked maximum Ambient temperature, we found that it was 34 degree.
Also we found that Winding Temperature is about 18 degree higher than Oil Temeperature.
My doubt is: Which is permissible maximum Winding Temperature Indicator reading? Is it 105 (=50+55)degree centigrade or 89 (=34+55) degree centigrade? Similarly which is maximum permissible Oil Temperature Indicator , 100 or 84 degree centigrade?
We have to set the alarm and trip settings to both Oil Temperature Indicator and Winding Temperature Indicator of the transformer. Please provide some suggestions in this regard too.
Thanks in advance,
zkz
We have recently installed a 15MVA , 66/11kv, Dyn11 transformer of which cooling is ONAN. Unfortunately we lost its manual from our station. When it was fully loaded we found that the Winding Temperature and Oil Temperature is compared other generator transformers in the same station. Which are ONAF and of different make. When we checked the name plate details we found the following details:
Maximum permissible Ambient Temperature: 50 degree Centigrade
Maximum Temperature rise above Ambient Temeprature for Oil/Winding: 50/55 degree Centigrade.
When we checked maximum Ambient temperature, we found that it was 34 degree.
Also we found that Winding Temperature is about 18 degree higher than Oil Temeperature.
My doubt is: Which is permissible maximum Winding Temperature Indicator reading? Is it 105 (=50+55)degree centigrade or 89 (=34+55) degree centigrade? Similarly which is maximum permissible Oil Temperature Indicator , 100 or 84 degree centigrade?
We have to set the alarm and trip settings to both Oil Temperature Indicator and Winding Temperature Indicator of the transformer. Please provide some suggestions in this regard too.
Thanks in advance,
zkz