Hi,
I'm trying to validate to which value I should size conductors going to a PMSM. The FLA of this motor will be 304A - and 308V (this is a high speed application, 24 000 RPM, continuous duty). Note that this voltage is developed at the motor which is driven by a VFD receiving 480V, 3 phases on the line side.
Obviously, NEC is mute on sizing conductors of such motors. Also, article 430 Part X only focuses on conductors feeding the power conversion equipment, not their load side conductors. Should I just look at Part II (430.22(B)) then and call it a day? That would set it to 125% of the FLA.
Thanks for your input.
I'm trying to validate to which value I should size conductors going to a PMSM. The FLA of this motor will be 304A - and 308V (this is a high speed application, 24 000 RPM, continuous duty). Note that this voltage is developed at the motor which is driven by a VFD receiving 480V, 3 phases on the line side.