PEMB Zee and Cee Purlins
NedHead
I'm trying to wrap my head around the design of light gauge Zee and Cee purlins in pre-engineered metal building design. I have the metal building systems book by Alexander Newman as well as the AISI manual and spec (newest edition of spec and the 2008 edition of the manual). Here's the set-up: fairly typical PEMB style building, 4:12 gable roof, 50'x90' long, steel frames at ~23' O.C. with Zee purlins spanning between frames. Standing seam insulated metal panel for the roofing, so I believe that means no diaphragm action (at least none you could really put numbers to).
With the sloping of the roof, you end up with weak axis bending in all the purlins, which normally would be taken out by diaphragm action, but in this case needs to be taken out to the steel frames through the weak axis alone. Even with really solid bracing between purlins (cold form channels at a reasonable spacing) you'd still be loading the purlins in the weak axis. As such I can't seem to get reasonable purlins to calc out well. I've seen 12" zee purlins spec'd at 20+' lengths and 4' spacing with higher snow loads than I'm currently working with on plenty of PEMB drawings, how do they do it? Are their systems using some diaphragm action they've arrived at through testing? Or diagonal metal strapping across the bays to take the load back the main steel frames (not a detail I've seen on any of the PEMB shops I have). Or is this just ignored when the roof slopes are low-ish
Wouldn’t the pre insulated panel act as a diaphragm
The types of insulated metal panels that I've been pointed towards by the architect all seem to have slide clips that don't allow for shear to transfer panel to panel. The few other IMP roof systems I've looked at all seem to be a similar situation which would negate any diaphragm action
Not really an answer but a comment. A lot of smaller metal buildings are not designed or certified by engineers, just "building designers" for companies like Mitek or others with proprietary metal building software. These structures get pawned off to the lowest bidder in such a way that all liability related to design criteria is removed from said designer. So, if you are wondering about how a metal building works, the answer is it probably doesn't.
That being said, rationally approaching the structure means that the hundreds of fasteners in the tin can 29 gauge diaphragm in conjunction with weak axis bending of the purlins must be the only way that load parallel to the frames get transferred from the roof , through the clips on the frame, into the frame and then through the moment frame to the (hopefully) engineered foundation.
When I design metal buildings I use a metal roof deck with actual capacities and analyze the connections from the deck to the frame. Of course, this is probably why I don't have a lot of metal building clients.
While a 4:12 may be a "standard offering" roof slope for many, a lot of PEMB roof structural logic was based on lower slopes (0.5:12 and 1:12). Somehow people have extended the design "logic" to 4:12s. I have seen many design calcs as if the purlins were 0:12 and then used on a 4:12 building. I have even seen it for a 6:12 once. Hanging point loads on 4:12s can be a more serious issue than 1:12s.
Zs have weak axis bending even on lower slopes.
I have not seen the panel thicknesses used in recent years, but minimum 26 gauge was a more common offering in the past. Rarely was anything less than 28 gauge used. 28 gauge was not a popular choice in earlier years. I have no idea how thin they are stretching things now.
First, who is the supplier you are working with for material sizes? Are you trying to piece together a PEMB from various component suppliers? If so, get their data first before you calc you own. There are so many more parameters involved in CFS than mill steel. Supplier criteria is not a constant.
If your roof panel is on "floating clips" for expansion, to my knowledge it has never been modeled as a diaphragm. Only a direct screw down is used for a diaphragm, and it is limited.
Also, are your Zs simple span or continuous? That may make some difference.