While the PEMB supplier says there is no moment, most all baseplates have some moment present. What you are depicting relates to where the PEMB supplier has "modeled" where the V and H occur on the baseplate. If the location is centered on the bolts, no eccentricity. If not, eccentricity. Well, the PEMB supplier probably has not specified the information in that much detail. We all know the model said it was pinned, therefor, no moment was calculated. For purposes of design, the depth was practically 0 in the model."
To answer your original question, you have eccentricity from vertical loads. You also have some 'unspecified' moment because the baseplate is not truly pinned. Next question, "How much eccentricity and how much unspecified moment?". The the more resistant you make you portion, the more the unknown values will be.
The true fixity of the connection has several parts to it and you do not have control over some of them if you are strictly designing the foundation.
[li]Depth of column (supplier)[/li]
[li]Bolt diameter, pattern and its location inside the profile of the column (supplier) (supplier tends to keep them the same relative to girt line)[/li]
[li]thickness of baseplate (supplier)[/li]
[li]welding of column to plate (supplier)[/li]
[li]foundation dimensions (you) (can make it more resistant to moment) [/li]
[li]bolt embedment (you) (no affect on resistance to moment but has an affect on bolt failure)[/li]