@delagina - Your second post - Can ACI section 14.3.6 be used? ACI defines wall as a member used to enclose or separate spaces. ACI does not give definition of a column based on the ratio of the cross-sectional dimensions. We have typically used UL Fire Resistance Directory classification, namely, cross-sectional ratio greater than 4 to distingush a wall from a column for design purposes.
For lightly loaded pedestals, not part of LLRS, and not in a high seismic zone, we only use outer ties at 12" o.c. We don't provide cross ties etc. However, we do show 3 ties at 4" o.c. at top of the pedestal.
Some time back I had posted a similar thread507-312673. I did not get much of a response.