Here's a little repeating nuisance problem that I keep seeing, thought I'd throw it out in case someone here's come up with a practical solution;
On a lot of gas wellsite facilities involving compression, produced water and hydrocarbon condensates (C5+) are knocked out of the gas stream prior to compression. The two liquids are then either dumped to tank(s) on site and are trucked out, or one or both are injected back into the gas downstream of the compressor for separation downstream. This is usually accomplished with a blowcase or a pump, in the latter case usually a simple motor driven packed plunger pump if power is available at site, or a pneumatic powered pump if not.
Because of the potential pressures developed by the motor driven recip, (pneumatics are usually self limiting as long as the pneumatic air/gas supply has overpressure protection) PSV's are required on the pump discharge to protect against overpressure due to blocked flow. Where I've been having fun lately is discovering a number of these installed in the field with the a conventional PSV that exhausts back to pump suction. Picking some arbitrary numbers for the sake of 'for instance', let's say 300# ANSI suction piping, 600# ANSI discharge piping, operating at ambient temperatures with design pressures of 740 and 1480 psig, respectively. I arrive on site and discover a conventional PSV set at 1440 psi exhausting back into the suction. Since a conventional PSV operates on differential, the discharge pressure could in fact be as high as 2180 psig before the PSV opens.
I've employed a variety of means to correct this, depending on the situation. In one case, due to a delining field the 600# discharge piping only operated at about 400 psig, and the 300# suction piping at 100 psig. I was able to drop the PSV set point on suction piping that I was able to set a conventional PSV at a practical pressure and still cover all operating cases. In another case, I was able to re-route the exhaust of the PSV to an atmospheric tank, in a third case, to a flare knockout equipped for fluid retention.
I'm thinking my only alternative in situations like this, which will allow me to discharge a pump PSV based on actual discharge pressure back into pump suction, regardless of suction pressure, is installation of pilot-operated PSVs. Any thoughts on the matter from the pump gurus? Bear in mind this is natural gas field production, so suction & discharge pressures are frequently all over the place.
On a lot of gas wellsite facilities involving compression, produced water and hydrocarbon condensates (C5+) are knocked out of the gas stream prior to compression. The two liquids are then either dumped to tank(s) on site and are trucked out, or one or both are injected back into the gas downstream of the compressor for separation downstream. This is usually accomplished with a blowcase or a pump, in the latter case usually a simple motor driven packed plunger pump if power is available at site, or a pneumatic powered pump if not.
Because of the potential pressures developed by the motor driven recip, (pneumatics are usually self limiting as long as the pneumatic air/gas supply has overpressure protection) PSV's are required on the pump discharge to protect against overpressure due to blocked flow. Where I've been having fun lately is discovering a number of these installed in the field with the a conventional PSV that exhausts back to pump suction. Picking some arbitrary numbers for the sake of 'for instance', let's say 300# ANSI suction piping, 600# ANSI discharge piping, operating at ambient temperatures with design pressures of 740 and 1480 psig, respectively. I arrive on site and discover a conventional PSV set at 1440 psi exhausting back into the suction. Since a conventional PSV operates on differential, the discharge pressure could in fact be as high as 2180 psig before the PSV opens.
I've employed a variety of means to correct this, depending on the situation. In one case, due to a delining field the 600# discharge piping only operated at about 400 psig, and the 300# suction piping at 100 psig. I was able to drop the PSV set point on suction piping that I was able to set a conventional PSV at a practical pressure and still cover all operating cases. In another case, I was able to re-route the exhaust of the PSV to an atmospheric tank, in a third case, to a flare knockout equipped for fluid retention.
I'm thinking my only alternative in situations like this, which will allow me to discharge a pump PSV based on actual discharge pressure back into pump suction, regardless of suction pressure, is installation of pilot-operated PSVs. Any thoughts on the matter from the pump gurus? Bear in mind this is natural gas field production, so suction & discharge pressures are frequently all over the place.