Therefore you want the ability to go to full load with all CVs opening together, instead of the CV opening seqential (one admission CV timing). If the boiler requires the CVs to control flow (pressure control), then all CVs will be modulating (throttling losses and controls stabilty).
Another advantage of FA is that the turbine first stage temperture differance from low load to full load is less than in PA (miltiple admission CV timing). (low load FA is hotter) Therefore, with the same ramp rate, the loading rate can be faster.
With the electronic controls, it is possible to have the ability to run with both one admission and multiple admission timing (Admissision Mode Selection). For example with 4 CVs, all 4 open together for startup and loading ramps, then a transfer to PA is used to fully open CV 1, 2 and 3 (no throttling losses for effeciancy) and only CV4 throttling for flow controll.
With the unit details, the expected efficancy losses (and $) for operating FA can be calculated.