Hello KKADM,
Yes you can do that, but take account the DOL Curent will be greater than PW Start.From the U.S Electrical Motors technicall Information : "This method used only a portion (usually one-half, but sometimes two-thirds) of the motor winding, increasing the impedance seen by the power system. It is to be used only for voltage recovery, and must not be left on the start connection for more than 2 to 3 seconds. The motor is not expected to accelerate on the start connection, and may not even turn.
Part Winding Start
Starting Characteristics:
1. Starting current is 60-75% of normal, depending on the specific winding connection.
2. Starting torque is very low (may not even turn the shaft).
3. Winding heating is very high on start connection.
Applications:
Where power system has automatic voltage recovery and normal inrush would cause unacceptable voltage dip. Should not stay on start connection more than 2 to 3 seconds"
Regards
Petronila