Parapet C&C - Internal Pressure
bdlc2k
26
Hey everyone
For building h<160ft, does anyone have a good example of what constitutes a porous vs non-porous parapet for C&C loading? What type of parapet would you apply +/-GCpi = 0.18 or 0.55? I can see how a CMU wall or tilt wall may have GCpi=0. What about metal stud parapet?
Most examples is see simply state they are using GCpi=0, non-porous with no real explanation. I read somewhere that internal building pressures may reach the parapet.
Thanks!
I think you need to provide the "reference" you read, so people realize what is your question and concerns.
Review section C29.5 of ASCE 7-16:
For parapets, regardless of porosity, I've never accounted for internal pressure or suction since it has pressure/suction on both exterior faces. If pressure/suction were to be present inside of the sheathing, it would cancel out on the global design.
jayrod12 - correct- this internal pressure question really only applies to the design of the parapet cladding and its fasteners.
Fair enough on the cladding attachment. I'm not sure how ASCE handles it, but in our case the NBCC it would classify as category 1 likely therefore minimal contribution to applied loading. And if it were so porous to classify as category 2 or 3, you may as well design the cladding for the same loads as the main structural components.
Yes - after typing my answer above I also should state that I've never worried about internal parapet pressures at all.