Maximum load is 80 kva or so, now what if i do this instead of 1 80 kva ups?
If the load is approximately 80 kVA then you certainly shouldn't be using a UPS rated at 80 kVA. Normally about 80% is the maximum amount of steady state load that you want to apply to a UPS - so in this case a UPS rated at 100 kVA would be a better option.
ups type is online and if i use 2 x40 kva ups it will cost less
No it wont, not if both the 80 kVA and the 40 kVA units are of the same technology and with the same battery autonomy (back-up time) specified. As the UPS size increases, the cost per kVA decreases.
Also the installation costs for two UPSs rather than one will be considerably higher.
and i think this will be more reliable,
No. If it takes both UPSs to run the load then the failure of one UPS will mean that the load will transfer to the bypass (reserve) supply. Effectively you are halving your mean time between failure (MTBF). So in effect, under this scenario, your reliability is halved.
There should only be two scenarios where parallel UPS systems are used:
1. For redundancy. The failure of one module doesn't effect the system as a whole and the site remains on UPS power (N+1).
2. Upgrading. On sites where the existing UPS has reached its limit another UPS can be placed in parallel to increase power.