I have a question regarding the application of ASCE 12.8.7. Equation (12.8-16) in ASCE 7-10 is as follows:
Theta = (Px) * Delta
Vx * hsx * Cd
Px = Total Vertical Design Load at and above level x
Delta = Story drift occurring simultaneously with Vx
Vx = Seismic Shear at level x
hsx = story height
Cd = deflection amplification factor
Calculation of Theta max is based on Equation (12.8-17):
Theta(max) = 0.5 / (Beta * Cd)
Beta = Ratio of Shear Demand to Shear Capacity for the story
ASCE also noted that theta should not exceed 0.1, which is around Theta(max)
Assuming Beta = 1.0 as permitted and Cd = 5.5, I have my Theta(max) = 0.091
I have the following sample of data from my coworker:
Level 30: P = 140 746 kN, V = 3758 kN, Delta = 6.653mm, h = 3200mm
Level 20: P = 257 772 kN, V = 4579 kN, Delta = 6.659mm, h = 3200mm
Plugging in these data, I get:
Level 30: Theta = 0.0142 < 0.091 [OK]
Level 20: Theta = 0.0213 < 0.091 [OK]
However, my coworker insists on following SEAOC Seismic Design Manual Example 17, where they ignored the Cd in calculating Theta getting the following results:
Level 30: Theta = 0.078 < 0.091 [OK]
Level 20: Theta = 0.117 < 0.091 [NG]
Why did we ignore the Cd value in SEAOC ?
Vx * hsx * Cd
hsx = story height