To me, the issue is less about the capacity of the circular footing (cuz it ain't a pier with a L/d of only 2...) than about whether it is reasonable to use lateral soil resistance within the "normal trenching depth" of 6 feet or so. Will the pole be well outside any public ROW and at least 10 feet from any buried utilities? Can you assure yourself that no one can excavate within 5 or 6 feet of the edge of the footing for the next 20, 30 or 50 years? In most cases, the clear answer is 'No' to one or both of those questions, and the footing would be considered as inadequate regardless of whether the calculations say the pole will stand up.
You have two other things to consider: the depth of seasonal change in soil moisture, and allowable tilting of the light pole. Since you're in Georgia, I suspect that the depth of seasonal moisture is greater than 4 feet. (I don't have any first-hand knowledge of how deep it is, but your area is subject to drought conditions so it's greater than 2 or 3 feet...) Significant moisture changes will affect the soil around the pole. Too wet, and the soil softens - the pole leans. Too dry, and the soil shrinks away from the footing - the pole leans. (You can't win for losing.)
And such a small footing will experience a lot of rotation before it develops enough soil resistance to resist those 20 kip-feet of moment. An inch of groundline deflection will result in almost 2 degrees of rotation. That's very noticeable. And 2 degrees of rotation may cause your moment to increase significantly...
(That light pole foundation is a bigger deal than you probably thought -)
Finally, I did not check your calculations to see if the footing has enough capacity. I suggest that you completely re-think your approach to the problem. Hire a geotechnical engineer to design the foundations for you. I doubt s/he designs lighting systems, HVAC systems, etc. Know your own limits - and hire an expert. It's likely that if you are working on a commercial site, and the owner has already hired a geotechnical engineering firm. Talk to them - I doubt they bite!
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips Fora.