Elmotor says "If the short circuit happens on the motor terminals, the drive will try protect itself (IGBT's) with fast overcurrent protection and will not create high torque". I need to correct that.
It is obviously not an external current (from the VFD) that causes the damaging torque. Instead, it is the internal EMF in the motor that does so. The EMF is a result of the DC flux that exists in the rotor and is locked in by the rotor bars. When there is a short across the motor terminals, a strong torque - initially equal to, or higher than, the starting torque - is developped. The torque is quickly reduced as the rotor flux is reduced and will exist for tens of milliseconds for rotors with a high R/L ratio and hundreds of milliseconds for rotors with a low R/L ratio.
So, the phenomenon exists. Regardless of how the motor is supplied - genset, DOL or VFD - no difference if the short is close to the motor terminals.
For Milovan: Waross' last paragraphs are worth reading once more. If the supply is weak, you can start the motor without any torque problems. But a bolted short across the motor terminals will cause problems.