Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations 3DDave on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Overstrength Factor in Anchor Design for Seismic Loading - Vertical Process Vessel

Status
Not open for further replies.

bones206

Structural
Jun 22, 2007
2,000
There is a bit of debate in my office and I am currently in the minority. My boss and others think that we should design the anchor bolts for a 90 ft tall process vessel (SDC C) using the overstrength factor option of ACI 318 Appendix D/Ch17. My understanding is that the overstrength method of designing anchors for this specific situation is prohibited by ASCE 7-10, Section 15.7.5:

15.7.5 Anchorage
Tanks and vessels at grade are permitted to be designed without anchorage where they meet the requirements for unanchored tanks in reference documents. Tanks and vessels supported above grade on structural towers or building structures shall be anchored to the supporting structure. The following special detailing requirements shall apply to steel tank and vessel anchor bolts in SDC C, D, E, and F. Anchorage shall be in accordance with Section 15.4.9, whereby the anchor embedment into the concrete shall be designed to develop the steel strength of the anchor in tension. The steel strength of the anchor in tension shall be determined in accordance with ACI 318, Appendix D, Eq. D-3. The anchor shall have a minimum gauge length of eight diameters. Post-installed anchors are permitted to be used in accordance with Section 15.4.9.3 provided the anchor embedment into the concrete is designed to develop the steel strength of the anchor in tension. [highlight #FCE94F]In either case, the load combinations with overstrength of Section 12.4.3 are not to be used to size the anchor bolts for tanks and horizontal and vertical vessels.[/highlight]


The underlying philosophy as I understand it is to force the anchors to be the ductile "fuse" of the foundation/anchorage system in order to promote bolt yielding, which absorbs the seismic energy hysterically and helps avoid a brittle-type failure or foundation overturning. I've read the ASCE

Does anyone know if there is an alternative approach where the overstrength factor method can be utilized, that is also code compliant? In other words, am I wrong or is my boss wrong? Either way I lose [thumbsup2]
 
Replies continue below

Recommended for you

I agree with Sandman21. Design the anchor for full tensile strength. No need to use the overstrength factor. It'll likely take reinforcing designed to carry the anchor load. I've used the paper "Design of Anchor Reinforcement in Concrete Pedestals" by Widianto, Patel, and Owen.

 
Ok, but do you agree that the overstrength factor is explicitly prohibited unless the vessel is SDC B?
 
Section 15.7.5 for the anchorage of tanks, specifically prohibits the use of overstrength. ACI Ch. 17 has four methods to satisfy 17.2.3.4.3. Section 15.7.5 for the most part is following option a. As a compromise design the anchorage per 17.2.3.4.3(a)
 
Thanks -- that's been my argument as well, but I wanted to throw the question out there to make sure I wasn't missing some other loophole or misinterpreting something in the code.
 
So the only time overstrength factors listed for tanks and vessels are used is for the design of connecting elements like anchor chairs, or compression struts in support towers (as per 15.7.3), correct?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor