I am dealing with a retrofit project where an existing training room (approx.1025 sf) was modified to 5 office spaces (approx. 950 st). The existing roof-top unit (RTU) is a 7-ton constant volume unit (DX cooling). It originally supplied approx. 2,400 cfm to the training room. The system has been modified with VAV boxes to control space temperature in the offices and a by-pass box added to the RTU to maintain a constant duct static pressure. The bypass box is discharging in the ceiling plenum ducted toward the return side of the RTU. The problem is that the offices have significantly less loads than the training room and a total design airflow of only 700 cfm.
I am wondering if there going to be any issues when cold supply air discharges through the by-pass box back into the unit in regards to the DX coil?
Would it make a difference if the by-pass discharges into the plenum away from the RTU return air opening? Any other thoughts/comments?
Thanks
I am wondering if there going to be any issues when cold supply air discharges through the by-pass box back into the unit in regards to the DX coil?
Would it make a difference if the by-pass discharges into the plenum away from the RTU return air opening? Any other thoughts/comments?