SKahle89
Chemical
- Sep 25, 2008
- 15
All,
First let me preface this post by stating that I am in no way an electrical engineer. My experience with motors and electricity is limited; so please respond in a way that typical engineer could understand.
I have a very oversized motor driving an reactor agitator. The agigitators were changed back in the 1970's, but the project manager chose not to replace the motors. The new agitators require a 75HP motor; the existing motors are 150HP. I grabbed my I&E tech and hooked up a portable power meter with very disturbing results:
HIGH-SPEED
POWER
kW 17
kVAR 17
kVA 71
PF 0.216
VOLTAGE
V AN 283
V BN 283
V CN 283
V AB 485
V BC 485
V CA 485
AMPERAGE
A N 162
A A 83
A B 84
A C 85
Notice the power factor of ~0.20. As everyone knows, energy reduction is a hot topic in industry right now. My question is, if I replace these motors with more appropriately sized ones, am I going to realize any savings due to decreased reactive load? Obviously there is some savings to be had by upgrading to a new high efficiency motor, but I am asking specifically about reactive load/power factor improvement. Thanks!
First let me preface this post by stating that I am in no way an electrical engineer. My experience with motors and electricity is limited; so please respond in a way that typical engineer could understand.
I have a very oversized motor driving an reactor agitator. The agigitators were changed back in the 1970's, but the project manager chose not to replace the motors. The new agitators require a 75HP motor; the existing motors are 150HP. I grabbed my I&E tech and hooked up a portable power meter with very disturbing results:
HIGH-SPEED
POWER
kW 17
kVAR 17
kVA 71
PF 0.216
VOLTAGE
V AN 283
V BN 283
V CN 283
V AB 485
V BC 485
V CA 485
AMPERAGE
A N 162
A A 83
A B 84
A C 85
Notice the power factor of ~0.20. As everyone knows, energy reduction is a hot topic in industry right now. My question is, if I replace these motors with more appropriately sized ones, am I going to realize any savings due to decreased reactive load? Obviously there is some savings to be had by upgrading to a new high efficiency motor, but I am asking specifically about reactive load/power factor improvement. Thanks!