Oversized holes
stillfan
I have two instances where I have an oversized hole with a bolt that is 1/4" to 3/8" oversized. The first is an anchor hole, there is a 3/4" bolt in a 1 1/8" hole. If I have checked the bolt and base plate to resist the shear, fatigue is not an issue due to the low frequency of the building and there is a washer that covers the hole for uplift resistance, have I performed an analysis that will cover all aspects of an oversized hole concerns?
The second location is a purlin connection. The purlin is an axial member, so again a check for shear on the bolt and shear block on the member, as opposed to a bearing situation and fatigue analysis( once again not a concern due to the low frequency of the structure). There is no tension force on the bolt so the washer pullout is not a concern. All these parameters are meet are there any other areas of concern if the washer is not welded to the member?
It is common to have oversized bolt holes for baseplates/foundations bolts and purlins.
Agree with kikflip that oversized holes are common practice for column baseplates and purlins. However, if you want a column to resist a significant horizontal load at its base, a different detail is required. Site welding on plate washers is one way.
I don't like using purlins to resist axial loading, although I know some people do it.
I agree with kikflip and hokie - These oversized holes are common for baseplates (See Table 14-2 on page 14-21 of AISC 360-05). 1 1/8" actually seems a little small for a 3/4" diameter anchor rod (I'd expect 1 5/16").
I also agree with hokie that the you need to provide a plate washer (with a standard hole) that gets field welded to the baseplate to take out the shear (if that is the load path you choose to use).
Without welding plate washers, your connections might not comply with AISC 360-05. This specification allows oversized holes in slip critical connections. However, your hole size is larger than the "oversized" holes in the specification. I am curious why you do not need to check for bearing.